Thanks again - I’ll take a look at the return temp if it’s possible to see it in a config menu shortly.By calculation 38kw at T60 is 27.7kw (T47), so you can add 14.1kw (of T60) = 10.3kw (T47 at 70C).
Rads need balancing or/and pump speed/head increased.
As above, if the boiler flowtemp is 70C. What is the boiler return temp?, you may see it in one of the menus.
If I add that many rads then put it back to full temp though, in real life terms what will happen? Boiler damage?