Hello,
Just wanted too double check everything is as it should be with bonding in Bathroom.
For reference only my sockets have RCD lighting doesnt.
Currently a radiator in my bathroom is going to be replaced by a towel heater (non electrical). The radiator is fed by copper pipe and has a wire attached directly to the radiator.
My mains cold feed comes into thee bathroom then has copper pipe with plastic fittings. Like this:
Mains Copper --- Push Fit Plastic Stop Cock --- Plastic Tee --- 1 Way to tap 1 way to bath.
Hot water is comes from floorboards ans same again goes to plastic fittings with copper pipe.
The hot water pipe is bonded at the hot water cylinder outlet (the same with cold mains).
Hopefully that explains the setup now some questions.
1. a) Does the new Towel radiator need the bonding cable attached to the old radiator need connecting to the towel radiator? b) is connecting it to the flow pipe enough?
2. Should my mains cold water have bonding after the plastic fitting?
3. Should the hot water have bonding after the plastic fitting?
Cheers
Just wanted too double check everything is as it should be with bonding in Bathroom.
For reference only my sockets have RCD lighting doesnt.
Currently a radiator in my bathroom is going to be replaced by a towel heater (non electrical). The radiator is fed by copper pipe and has a wire attached directly to the radiator.
My mains cold feed comes into thee bathroom then has copper pipe with plastic fittings. Like this:
Mains Copper --- Push Fit Plastic Stop Cock --- Plastic Tee --- 1 Way to tap 1 way to bath.
Hot water is comes from floorboards ans same again goes to plastic fittings with copper pipe.
The hot water pipe is bonded at the hot water cylinder outlet (the same with cold mains).
Hopefully that explains the setup now some questions.
1. a) Does the new Towel radiator need the bonding cable attached to the old radiator need connecting to the towel radiator? b) is connecting it to the flow pipe enough?
2. Should my mains cold water have bonding after the plastic fitting?
3. Should the hot water have bonding after the plastic fitting?
Cheers