This was on earlier post 2011
It's a rebadged Drayton Digistat SCR.
Try this. If it doesn't work, check battery terminals are clean. Still not working.................new stat time.
1. Turn off the power supply to the Digistat SCR (receiver unit)
and leave for 5 seconds.
2. Turn on power to SCR unit and check red light is on.
3. Press override button No.2 and check the green light comes
on and boiler fires.
4. Press & hold down button No.1 (Keep depressed), then
press No.2 and keep depressed. {The Red LED light will flash
a couple of times and then it will go out}
5. Now release both the buttons – {the two LED lights should
come back on}
6. Get the Digistat+2RF/+3RF unit and stand two metres away
from the SCR unit with the Digistat+2RF/+3RF unit in your hand.
7. Remove the battery cover and fit the batteries.
8. The Red LED light on the SCR will now flash for approx. 7
seconds.
9. This confirms that the radio signal is being sent and
received.
10. The Digistat+2RF/+3RF and the SCR are now successfully
linked by a dedicated RF address
Read more:
//www.diynot.com/forums/plumbing/british-gas-wr1-wireless-thermostat.294452/#ixzz2w4iZ2bVn