I know the components need to be disconnected Tony, that's why I made reference to my initial test results, then I just wanted to prove that the cell was light responsive, or not. Tonights test was only on the two photocells, unplugged and I even held them in the same place to try and get a reasonably consistent light for both tests!

The boiler is a Trianco Eurotrader. You can guess from my moniker where I live, fancy coming up and setting up my boiler Martin? Hahaha.

Cheers to both
 
Sponsored Links
You said you have a 0.65 80S nozzle, oil pressure should be set at 140 psi CO2 set at 11.0%.Smoke reading 0-1 Flue gas temp 200 Degrees and air will just have to be adjusted to suit, so ya will need a FGA. Best call an engineer buddy.
 
Thanks for all the advice Martin, much appreciated. I'll call someone in and get it set up.

Cheers
 