522.6.4 A wiring system buried in a floor shall be sufficiently protected to prevent damage caused by the intended use of the floor.
522.6.5 A cable installed under a floor or above a ceiling shall be run in such a position that it is not liable to be damaged by contact with the floor or the ceiling or their fixings. A cable passing through a joist within a floor or ceiling construction or through a ceiling support (e.g. under floorboards), shall:
(i) be at least 50 mm measured vertically from the top, or bottom as appropriate, of the joist or batten, or
(ii) incorporate an earthed metallic covering which complies with the requirements of these Regulations for a protective conductor of the circuit concerned. the cable complying with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436, or
(iii) be enclosed in earthed conduit complying with BS EN 61386 and satisfying the requirements of these Regulations for a protective conductor, or
(iv) be enclosed in earthed trunking or ducting complying with BS EN 50085 and satisfying the requirements of these Regulations for a protective conductor, or
(v) be mechanically protected against damage sufficient to prevent penetration of the cable by nails, screws and the like.
522.6.6 A cable concealed in a wall or partition at a depth of less than 50 mm from a surface of the wall or partition shall:
(i) incorporate an earthed metallic covering which complies with the requirements of these Regulations for a protective conductor of the circuit concerned. the cable complying with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436, or
(ii) be enclosed in earthed conduit complying with BS EN 61386 and satisfying the requirements of these Regulations for a protective conductor, or
(iii) be enclosed in earthed trunking or ducting complying with BS EN 50085 and satisfying the requirements of these Regulations for a protective conductor, or
(iv) be mechanically protected against damage sufficient to prevent penetration of the cable by nails, screws and the like, or
(v) be installed in a zone within 150 mm from the top of the wall or partition or within 150 mm of an angle formed by two adjoining walls or partitions. Where the cable is connected to a point, accessory or switchgear on any surface of the wall or partition, the cable may be installed in a zone either horizontally or vertically, to the point, accessory or switchgear. Where the location of the accessory, point or switchgear can be determined from the reverse side, a zone formed on one side of a wall of 100 mm thickness or less or partition of 100 mm thickness or less extends to the reverse side.
522.6.7 Where Regulation 522.6.6 applies and the installation is not intended to be under the supervision of a skilled or instructed person, a cable installed in accordance with Regulation 522.6.6 (v). and not complying with Regulation 522.6.6 (i), (ii), (iii) or (iv), shall be provided with additional protection by means of an RCD having the characteristics specified in Regulation 415.1.1.