I currently have a closed system boiler install, with 2 2 port motorised valves being controlled by HIVE.
Recently, the boiler doesn’t fire up when the central heating shedul is due on, I have changed the batteries in the stat, rebooted everything that can be rebooted, checked the where’d connections. If I turn off the power to the Hive receiver and back on again it kicks in. Sometimes when I press the boost or manual button it kicks in.
I have been told this could be a fault with the motorised valve, due to the micro switch in it sending a signal to activate the pump and boiler once open. The valve is clunky it doesn’t feel like the valve turns the motor or potentially opens the valve.
before I go pulling the valve apart, or purchasing a new one, I would appreciate any suggestions as to what might be wrong?
thankyou for your help
Recently, the boiler doesn’t fire up when the central heating shedul is due on, I have changed the batteries in the stat, rebooted everything that can be rebooted, checked the where’d connections. If I turn off the power to the Hive receiver and back on again it kicks in. Sometimes when I press the boost or manual button it kicks in.