Central heating issue

Joined
12 May 2026
Messages
7
Reaction score
0
Country
United Kingdom
I’ve got a central heating system that’s losing pressure.
The expansion vessel was repressurised to 1.5 and held that pressure. I’ve replace the prv to a brand new one also.
I’ve turned the boiler off and put the condensate into it and no water has come out.
No water is coming out of the prv drain pipe.
There are no visible leaks but I’m still losing pressure. Roughly 0.5bar every hour or so.
I have a Worcester 30cdi
 
If nothing out of prv or condensate waste and no obvious leaks on boiler , and you have re pressured a number of times look round system.
Rad valves are a favourite.
Any buried pipework?
There are definitely no leaks from rads or from pipework. I can see all the pipework apart from a couple small sections, but by now there would be stacks of water.
 
Pressurise the system to approx 2.5 bar, Isolate the boiler flow and return and unisolate the boiler after a period of 8 hours. If it drops before that it's the boiler, if it drops after that, it's the system.
 
Pressurise the system to approx 2.5 bar, Isolate the boiler flow and return and unisolate the boiler after a period of 8 hours. If it drops before that it's the boiler, if it drops after that, it's the system.
Thanks.
Where would it be leaking from the boiler. I have no water anywhere, same with the system. It’s really not making sense. Would a bottle valve trap inside the boiler that’s failed (not leaking water) cause any issues like this?
 
Do you lose pressure when the boiler is cold ( not been used for a few hours )and not in use at all for domestic hot water or central heating ?
 
Do you lose pressure when the boiler is cold ( not been used for a few hours )and not in use at all for domestic hot water or central heating ?
I’m pretty sure we do as it’s not been used and ends up empty, I can double check this.
Only things I haven’t replaced is the expansion, but again this let me pressurise it to 1.5 and the bottle trap.
The boiler is just heating. It has 3 zones, but two have not been active the last few weeks and are on those electronic isolation box things.
 
Just check and pressure back down to near 0, last filled it up around 5.30.
There is zero water anywhere, both overflows are dry as a bone too. At an absolute loss
 
Just check and pressure back down to near 0, last filled it up around 5.30.
There is zero water anywhere, both overflows are dry as a bone too. At an absolute loss
I'd try this.
Pressurise the system to approx 2.5 bar, Isolate the boiler flow and return and unisolate the boiler after a period of 8 hours. If it drops before that it's the boiler, if it drops after that, it's the system.
 
If you are losing pressure when the boiler isn't being used ,and nothing is coming out the boiler,it's condensate pipe,or the PRV's discharge pipe, that's indicative of a leak on the system. Is there any heating pipework buried in concrete flooring ,or a void under the ground floor?
 