Where do you change or see what settings the pump is on?. I have a feeling there might not be a Eco setting on that model.
"On CH the Pump gets quite noisy with a gurgling/gargling/bubbling sound which increases over time."
Even though no problems on HW (or refilling) would suggest checking where the vent and cold feed are teed in, if its the conventional (VCP) system where you have the pump on the boiler flow, with, from the boiler, Vent, cold feed, (no more than 150mm apart) then pump, a blockage/partial blockage can occur where the cold feed is teed into the system.
Is this a new problem since the last heating season?.
"On CH the Pump gets quite noisy with a gurgling/gargling/bubbling sound which increases over time."
Even though no problems on HW (or refilling) would suggest checking where the vent and cold feed are teed in, if its the conventional (VCP) system where you have the pump on the boiler flow, with, from the boiler, Vent, cold feed, (no more than 150mm apart) then pump, a blockage/partial blockage can occur where the cold feed is teed into the system.
Is this a new problem since the last heating season?.