I want to change / have altered the circuit in my garage. The garage is attached to the house (i.e. NOT separate, outdoors etc), and currently has a radial circuit (about 15m total length) wired with 2.5mm2 (surface clipped) T&E to a 16 amp type B MCB. The whole system is a TT, for reference (30mA RCD in situ).
This is inadequate for welding, except at the lowest current levels. I need to go up to a 30A nominal current draw, so was thinking in terms of 6mm2 T&E and a 32A type B MCB.
Based on my calcs. this is adequate. Any (helpful, please) comments?
My reading, since this is an upgrade to an existing circuit, not in a special location, is that this is NOT Part P notifiable. Comments?