Checking Earth

Joined
14 Jun 2005
Messages
372
Reaction score
8
Location
Worcestershire
Country
United Kingdom
Right, from a DIY point of view, you know if you change a the facia of a plug socket you can tell if the connections are ok because if they weren't the circuit wouldn't work.

Well how do you till if the earth connection is sound? Would the RCD trip, or do you need some kind of testing tool?
 
That's not quite true.

If it's on a ring (two "red" and two "black" wires, or brown and blue if recent, and two Green&Yellow) then one of each could have fallen out and it would still work.

If you are doing a rewire, you test for continuity with a simple meter and that will tell you if the ring is unbroken. If you have a low ohms meter you can test the resistance (which should be the same for the red and the black, and about 50% higher for the G&Y) which can indicate if there is anything else untoward. Rings do sometimes get broken, e.g. from a loose connection, or a damaged cable or accessory.

If you are just replacing a single socket, you can do a continuity test (the two reds will have continuity; the two blacks, and the two G&Y) which will tell you if you have an unbroken ring apart from the socket you have just removed.

I don't know a way to test that you have connected the new socket properly, other than by inspecting it carefully (unless you disconnect somewhere else). But I think that even for an amateur repair, it is a good idea and easy to test for continuity every time you take a socket off the ring, e.g. for replacement or when decorating. You can do this with a simple multimeter that should cost less than £10.

Continuity tests like this only work on rings, not on lighting or radials, or on spurs.

To get an idea if the earth is connected, you can use a plug-in socket tester which costs in the region of £8 and will be in your DIY store or hardware shop. These testers are not very precise though, and will only detect certain gross errors.
 
Your

Zs =Ze+(r1r2)

max Zs measured should be below the BS7671 figure according to mcb type and amp
 
HVMAN said:
Your

Zs =Ze+(r1r2)

max Zs measured should be below the BS7671 figure according to mcb type and amp

Zs = Ze+(R1+R2) :wink:
Measured values should be below the figures given in the OSG or GN3 (corrected for conductor temp), the max Zs figures in BS7671 are for design temp.
 