I am currently running containment for the garage electrical installation which will consist of 4-5 double sockets and 2-3 light fittings.
I have done some searching on the subject but just want to confirm the following;
1) Lights and power can be run on a single radial circuit "Garage Power & Light"
2) Doing this is compliant with current regulation (most threads I have read are from a few years back)
3) Can the light switch be the final link in the radial or does it need to be linked via a fused spur?
With regards to the containment is it just the drops from the roof void that need to be protected and not the cable runs within the roof structure?
Thanks in advance for any help provided.
That depends on the overcurrent device protecting the circuit. IIRC the maximum permitted for a lighting circuit is 16A, so if your radial circuit has greater than a 16A protective device you will need to fuse down for the lighting part. You must also ensure that the cable and switchgear used is appropriate to the size of the protective device. In most cases it is simplest to use a switched fused connection unit as the lightswitch.
That depends on the type of cable you are using. If you are using conduit singles, they must be entirely contained over their whole length because they have only single insulation. If you are using insulated and sheathed cable, such as T&E, you may use containment as you see fit for additional protection.