Classic Heating system not working properly

Joined
12 Oct 2012
Messages
2
Reaction score
0
Location
Derbyshire
Country
United Kingdom
Hello!
I hope someone can help me, I have a classic boiler and heating system which works like a dream when its on the timer which is twice a day.

But I press the manual button, mainly in the evening, on the main control nothing happens, the separate thermostat is set at the max, 30 degrees and when you move it I can feel it click but the heating still does not come on.

The strange thing is that when I have pressed the manual button and I run the hot tap for a while, the heating will then come on! its baffling me completely!

Please help! :D
 
sounds like you have an S plan system with two zone valves and the end switch on the CH one is faulty, when you run the HW the temp in the tank will drop and the HW valve will bring the boiler on
 