can someone explain what a clean earth is, when I search for answers all I get is stuff about saving the planet.
Such as Surge protected clean earth socket outlet?
Such as Surge protected clean earth socket outlet?
Chri5 said:Clean earths for telecoms was big in the 80's and 90's and used to have to be less that 0.5 ohms.
Clean earths for telecoms was big in the 80's and 90's and used to have to be less that 0.5 ohms.
Chri5 said:Do Telecoms clean earth still have to be run in cream cable with "functional telecoms earth" stamped on the sheath every metre?
Correct in the first part but then you go on to say it's connected to the Main Earth Terminal this is NOT a clean earth(connect a scope to it to see how noisy it really is).Chri5 said:Its an earth that is completely separate from CPC earths, bonding earths etc. A dedicated earth (or 'clean' earth) direct from the main earthing terminal (MET) of the property, normally it is also specified as being very low resistance.
Clean earths for telecoms was big in the 80's and 90's and used to have to be less that 0.5 ohms.
Wouldn't be available in a standard supply fed house.delta/star 1:1 transformer where the supply comes in three phase to the delta windings and the star windings
Chri5 said:Tim- In a domestic dwelling, what would you say constitutes a clean earth?
A seperate earth rod?
Wouldn't be available in a standard supply fed house.delta/star 1:1 transformer where the supply comes in three phase to the delta windings and the star windings
Isolated Earth/Ground
I ask you, with tears in my baby-brown eyes, how can one have an Earth or Ground that is isolated? If it were, then it would not be able to conduct noise or fault currents. Isolated means just that i.e. that there is no intended physical connection to other parts of the circuitry (and that includes via the ground itself!).
An Earth, in my books, starts in the shape of a flat copper bar 150mm wide by 0.5mm thick. This makes the cross sectional area 75mm², in other words a fairly substantial conductor. The DC resistance at 50Hz will be approximately 30mW per 100metres. But, the surprising thing is this is unchanged all the way up to 150kHz - unlike a similar round conductor that would have a DC resistance of 300mW i.e. 10 times this, by the time one reaches the same 150kHz!
The reason for this is the surface area of the 150x0.5mm is 301mm (don't forget the sides!). A 75mm² round cable has only 30mm of surface area i.e. 10 times less for the same amount of copper. Oh, if there is even an inkling of desire to use each individual strand and calculate the total surface area, well, you're just wasting your energy. The skin effect works by the overall diameter of closely spaced conductors.