hi guys .i have to fill water pressure every 4 minutes any ideas.water running out of pipe outside as soon as i start to fill loop :( :(
 
Your pressure release valve is jammed open!

So what are you going to do now?

Tony
 
wow that was quick,have got british gas coming to tomorrow or can it fixed easily or how long should it take an engineer to do it
thanks for the answer
 
wow that was quick,have got british gas coming to tomorrow or can it fixed easily or how long should it take an engineer to do it
thanks for the answer

just took it out and now instead of a consistant run is now only a drip
big big thanks to yourself
 
Even with a drip you'll still lose pressure. What pressure are you setting the water to when cold? Also what pressure does it rise to when heating is on?
I suspect expansion vessel has lost some or maybe all of its pre air charge so instead of operating form 1bar (cold) to 2bar (hot) it most likely going from 1bar to 4bar or more. But the PRV opens at 3bar to save the day!
It is suggested the 'air' charge of the vessel is checked if the water pressure is reaching near to 3bar.
 