Connecting Panel Heater

Joined
1 Mar 2005
Messages
53
Reaction score
0
Location
Stirlingshire
Country
United Kingdom
Have got a new panel heater here, first thing I notice is it only has a 2 wire cable with no earth, is this completely abnormal.?

"The installation must be equipped with an all pole diconnection mechanism with break contact distance of at least 3mm in each pole", what am I looking for in simple terms.?
 
Providing the heater is double insulated (which most are these days) then yes a two core flex is normal.

"The installation must be equipped with an all pole diconnection mechanism with break contact distance of at least 3mm in each pole", what am I looking for in simple terms.?

Depending on the installation either an FCU or a 20A DP switch

MKK1040.jpg


or

MKK5403.jpg
 