    I need some advice on the heater swap-out please.

    I want to install a 2.1kw storage heater where a 1.2kw storage heater used to be.

    We have a few panel heaters in the house and two storage heaters in one end. I want to swap the panel heater at the other end of the house with a storage heater.

    I'm in Scotland and on Total Control Heating. The panel heaters are all connected to a single MCB of 20A and it appears to me as if they're on a ring with both ends of the ring connected to the same circuit breaker.

    My plan is to disconnect the panel heat at the neon switch and put it's connections aside after insulating etc.

    I then want to run a 2.5mm cable from the distribution box directly to the storage heater.

    I want to run the cable in the underfloor cavity from the distribution box to the installed position, running the last 600mm up the cavity plasterboard wall.

    I want to connect the cable to a new 20A MCB which is fed from the TCH master circuit breaker. I'm thinking like this because the other two heaters are already on their own circuit breaker each.

    Is my thinking correct?

    And as an aside, why are earth wires inside switch boxes sleeved (insulated) and not left naked?

    I'll appreciate any comments on the above.
     
    Last edited: 25 Oct 2016
  2. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    35,771
    Thanks Received:
    3,999
    Location:
    Retired to:
    Country:
    Portugal
    Ok.

    They should each be on a separate circuit.
    Two small ones could be connected to the same MCB - although unusual.

    The panel heater may be on the same circuit as the sockets.
    If so, it may be better to fit a socket and a new accessory for the storage heater.

    Ok.

    That's ok, but 2.1kW is less than 9A.

    You said they were both on the same breaker.



    I have asked the same question myself. I don't know.
     
  3. Sponsored Links
  4. AlphaDog

    AlphaDog

    Joined:
    25 Oct 2016
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for your reply.

    You spotted an error in my question. It is the panel heaters which are on the same circuit breaker. The storage heaters each have their own MCB. I have edit the original question to reflect that.

    So, it seems OK then other than I should install say, a 15 Amp MCR instead of 20 amp?
     
  5. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    35,771
    Thanks Received:
    3,999
    Location:
    Retired to:
    Country:
    Portugal
    MCB - It doesn't really matter - 16A is usual for a storage heater.

    There are some complicated explanations but a standard 2.5mm² cable with 16A MCB will be fine.
     
    • Thanks Thanks x 1
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page