- Joined
- 10 Nov 2007
- Messages
- 162
- Reaction score
- 4
- Country
Following on from this thread:
http://www.diynot.com/forums/electr...btree-starbreaker-backward-compatible.353859/
New meter being fitted 20/02/2013 by DNO.
I'm going to supply some 25mm^2 tails and a switchfuse (cheaper than an isolator switch) and ask the engineer nicely if he wouldn't mind wiring to the switchfuse rather than the CU, and replacing the DNO's 16mm^2 cutout<>meter cables with 25mm^2.
On TheKeymeister's suggestion I'll send the DNO a photo of the cutout, and see if they fancy swapping it for a spunky new one with an 80A or 100A fuse rather than the existing 60A fuse.
Switchfuse:
http://www.tlc-direct.co.uk/Products/CGMSF100.html
The existing CU is obsolete, with blanking plates missing and no RCD protection on some circuits. A new one, fully populated, is relatively inexpensive:
http://www.tlc-direct.co.uk/Main_Index/Consumer_Units_Index/MK_17_Consumer_Units/index.html
It comes with 1x 40A, 4x 32A, 2x 16A and 3x 6A MCBs.
I can swap one of the MCBs for a 50A affair to take a 10.5 kW shower at a later date:
http://www.tlc-direct.co.uk/Products/MK5950S.html
As the cable size at 10mm^2 and either in it's own surface trunking, in uninsulated floor void, or buried in solid plaster, hence adequate, I could fit this from day one, correct?
Option 1:
Run the shower (50A, 10 mm radial), immersion (16A, 2.5 mm radial), and lights, (2* 6A, 1.0 mm radials) from one RCD.
Run the hob (40A, 6 mm radial), sockets (2* 32A rings), and electronic miscellaneous (alarms and CH, 1* 6A, 1.0 mm radial) off the other RCD.
This avoids lights going out when you're drilling through an electrical cable at the top of a ladder/jabbing a knife in a toaster at 4am, and splits the load across the (63A only) RCDs.
Option 2:
bernardgreen suggested keeping the shower separate from the main CU in the linked thread.
Run the hob (40A, 6 mm radial) and lights, (2* 6A, 1.0 mm radials) from one RCD.
Run the sockets (2* 32A rings), immersion (16A, 2.5 mm radial), and electronic miscellaneous (alarms and CH, 1* 6A, 1.0 mm radial) off the other RCD.
Run the shower off it's own 50A RCBO mounted in the same CU:
http://www.tlc-direct.co.uk/Products/MK7939S.html
Option 3:
As above, but take the output of the switchfuse to a double pole connector block/henley:
http://www.tlc-direct.co.uk/Products/MK1100.html
Then run an entirely separate CU fed by 25mm^2 tails just for the shower.
I'm less keen on this at you've now got three "isolator" switches, only one of which is guaranteed to kill your circuit whereas with 1&2 either main switch kills everything. More work/expense too.
Over to you, experts! Which would you recommend? Something different again?
Bonding:
At present, there's a pipe earthing strap clamp around the lead-sheathed incomer that runs to the E7 time clock (underneath the DNO's seals) and direct to the earth bar in the CU. There is no separate MET. No idea whodunnit.
There is an earth lead dangling in the cupboard, which ran from the CU earth bar to nowhere. I'm guessing that this used to bond a gas meter, and this used to live under the stairs but now lives outside. The current gas meter is not bonded at all, and is fed by a plastic sheathed pipe.
The water supply is a 15 mm OD copper pipe from underground. This is bonded to the hot water supply. The straps appear dirty, and they've used the strap as the connector across two clamps rather than a piece of wire. The earth cable runs back to the CU earth bar.
The CH is not bonded directly. It does have a bond via the hot water pipes <> heating coil in the HW cylinder <> boiler and CH pipes/radiators. I haven't got the gear to check impedances and haven't had this checked yet.
All the earth cable is 10mm^2 (same size at the shower cable). The meter tails are 25mm^2 but the cutout<>meter cables are run in 16mm^2.
The pipe strap around a lead sheathed incomer looks sketchy to me. Is it the DNO's responsibility to provide a good earth?
As I understand the regs, 10mm^2 is ok with 16m^2 meter tails, but if I have these swapped for 25mm^2 by the DNO chappie then all the earth bonding needs to be 16mm^2, correct?
I should bond cold, hot, and CH pipework (big metal towel rail in a bathroom with an electric shower). It might not need it/might bond adequately through the pipes but the delta cost is pennies and it'll save egg on face when the LABC checks it all out.
Gas meter bonding...
It's outside and the boiler, bonded by both it's (tiny) electrical supply and indirectly via it's flow/return pipes, is inside the kitchen about a metre away. I'm not too fussed about the safety implications of bonding this, as there's nothing within 2 metres that's powered except for the boiler's own (earthed, and fused at 3A) electrical supply. What are the rules though? Running 16mm^2 to this would be a right royal PITA, as its in the opposite corner of the house to the electrical gubbins.
Other:
-The house had an attic conversion with 4 double sockets daisy-chained (radial, or spur off a spur off a spur, how would you describe?) and hooked into the upstairs lighting circuit. Can I add a 13A fused faceplate to the ring main and hang the lot off the output of that? It'll be quick/dirty/good enough for a hairdryer.
-Is a shed fed in 2.5mm^2 by a 13A fused faceplate on the ring acceptable?
-Is a double outside socket fed by a 4mm^2 super off the ring acceptable? (it's the other side of a wall to an existing socket)
-Kitchen fitters have been present. Amongst many other kludges they've moved the cooker switch and to do so joined the supply with chocolate boxes, plastered over it, and stuck tiles over the top. I understand that connections need to be accessible now. The supply runs through the ceiling/floor void, then down the kitchen wall. Am I ok to cut this cable upstairs, and fit a junction box under the floorboards in the bedroom. (this is accessible by lifting the carpet/lifting a marked/non-screwed floorboard - adequate?)
Many thanks for your patience and sage advice if you've got this far!
For your horror/amusement I've provide a "double socket conversion" by the previous (Polish) owners:
IMAG0696 by markocosic-yahoo, on Flickr
IMAG0695 by markocosic-yahoo, on Flickr
Hey! They used tape at least...
Switchfuse:
Option 1:
Option 2:
Option 3:
Bonding:
Other: