without seeing it, be aware that the internals of different models of CU differ. The makers in structions are definitive, but in a split load box I'd expect to see two short busses, one linking all the non-RCD stuff to the main switch, and one linking the RCD protected stuff to the RCD.
BUT, I'd expect you to check this before starting the job, and consult with either the makers, or an electrician familiar with that model.
And, as others have noted, you should be checking the wiring you are connecting in to it , for earth continuity and insulation resistance at least, and ideally ring main integrity as applicable too.
regards M.