Is it compliant with BS7671 to have bonding that goes from the consumer unit to the water supplya nd then loops to the gas supply or do they have to be separate cables?
 
can be looped, providing the cable isnt broken
 
Hi

You can have an inline crimp in and providing the reading is less than 0.05 ohms then it is ok. I know it's not a preferred method but it can get you out of the doo at times.
 