Yes, I suppose that's got to be true to some extent, but there's hardly any difference between 1.35 and 1.38, so one might as well 'be conservative'! However, I also suspect that some of the small variation in the de-rating factors (from 1.39 for 1mm² {yes, fractionally higher than 1.5mm² and 2.5mm²} to 1.49 at 16mm²) may be as much to do with rounding as anything else.That makes sense. Now my understanding is the factor is less restrictive for 1.5mm2 because smaller conductors can dissipate heat better? Or is it the other way around? Correct to think that heat dissipation of 2.08mm2 is in between 1.5mm2 and 2.5mm2?
Kind Regards, John
OK, doing more research I came across this, not sure if it helps though, the tables used for countries that use 2.08mm2 wire. But it has me confused. At 75*C, 2.08 is listed at 20amps. I take it the conductor insulation is rated higher?
http://www.encorewire.com/wp-content/uploads/wire-size-table-CU.png
http://i.stack.imgur.com/V56uL.png
And the old table 310.16 before it was changed to the above: