1. This seems to me that the valve may not be installed correctly or possibly it is not working at the right/expected temperature?2. Can a radiator work correctly with the hot water coming in from the wrong end first???
I am looking at the diagrams on the link provided earlier when I ask question 2 above.
http://heating.danfoss.com/PCMPDF/013R9355_RAS_C2_Keymark_VISXM302_.pdfHave you tried swapping the TRV head for another one?
- If it is the Danfoss RAS-C2, then yes it is can go on either end - as shown in the link's diagrams. Setting the flow adjuster may help.
- There is no right and wrong end on a typical radiator (there are exceptions, e.g some vertical designer rads). All the TRV does is control the flow through the radiator.
Hi, as mentioned early, I cannot get down to do anything like this, I cannot even plug a mains plug in at standard low level.
Once I know what is wrong and how we can get round it, it seems we are getting much closer now. I can get heating engineer/plumber service the boiler and ask him to check the radiator for us.
Many thanks for your help and information provided.