Sorry to butt in.
If it prooves difficult to measure Ze, ( for difficult I mean potentially dangerous for flat above, and sorry to keep going on about the flat above) is it sufficient to use the "by enquiry" value. This is for my assesment and I want to get everything just right.
Yes, it's acceptable to use figures from enquiry (0.35ohms PME, 0.8ohms TNS).
If you can't isolate the supply to remove equipotential bonding whilst carrying out a Ze test then you have no other option.