DHW heated by modern CH boiler, what stops it cooling it?

Joined
27 Jan 2008
Messages
29,735
Reaction score
3,680
Location
Llanfair Caereinion, Nr Welshpool
Country
United Kingdom
It does not affect me, as I don't have a condensing boiler, but the whole idea today is to vary the water temperature rather than simply turning boiler on/off.

So I know we want DHW stored at over 60ºC, but not much more, but how does it ensure the boiler warms DHW and not cool it?
 
Thank you, I assume that means there needs to be some wiring to say either CH or DHW, this is clearly built in with a combi boiler, but with a system boiler, it would need extra wires, so all my wiring diagrams for S and Y plan must now be redundant? I assume C plan is simply no longer used?
 
There are various ways of doing it. Some controllers have it built in now and some boilers use an NTC sensor and so it natively

Any boiler that can use weather compensation or opentherm can be made to work on priority hot water as can individual makes like Worcester which is why you need to use their own controls
 
Thank you, I assume that means there needs to be some wiring to say either CH or DHW, this is clearly built in with a combi boiler, but with a system boiler, it would need extra wires, so all my wiring diagrams for S and Y plan must now be redundant? I assume C plan is simply no longer used?
Look up X plan designed for hot water priority.
C plan was very rarely used (in this area anyway) fully pumped S plan way more normal.
Y plan is horrible for several reasons!
 