Disconnected cable inside garage fuse box

But what concerns me more is that brown/black/grey usually indicates an armoured cable, armoured cables are usually terminated with a gland that restrains the cable and earths the armour. It sounds like this installation may have been a lash-up from the start and is in need of some remedial work beyond reconnecting the grey wire.
For a start it depends on if the armour actually requires an electrical termination or mechanical restraint at that point. If not it can simply be dealt with like any other cable, such as T&E
I'm assuming the earth sleeved black at top right is the 3rd core and hope the armour is earthed at it's source.

One situation where the SWA gland caused a hazardous situation
1756372835400.png


My solution to removing the hazard:
1756372863995.png
 
Hi guys, I have a garage fuse box installed a few years back by a qualified electrician with a 3 core cable from the house consumer unit. All has been ok and
A good few years back - or many years back - would presumably be much more accurate...
 
Time flies Risteard, about 10 years ago lol, electrician now lives and works in Dubai, lucky git:)
 
For a start it depends on if the armour actually requires an electrical termination or mechanical restraint at that point. If not it can simply be dealt with like any other cable, such as T&E
I'm assuming the earth sleeved black at top right is the 3rd core and hope the armour is earthed at it's source.

One situation where the SWA gland caused a hazardous situation
View attachment 391022

My solution to removing the hazard:
View attachment 391023
There is no gland etc that I can see, the armoured cable just comes through the old concrete wall about 2 feet from the consumer unit. It has then been stripped down to the inner sheath from there, and then stripped to expose the cables that enter the consumer unit.
 
I'll look again tomorrow and try another photo, thanks
Hi all, here is 2 better photos of the wiring at the top of the consumer unit. (including my shoes!)
I have undone the brown cable and reattached it properly, the missinggrey cable hasn't been reattached in the photos yet, but it should go from the Neutral on the left of the brown cable to the securing screw in the Neutral bar above it?
All the other cables are in original position and haven't been moved
IMG_0402[1].jpeg
IMG_0402[1].jpeg

IMG_0402[1].jpeg
 
the missinggrey cable hasn't been reattached in the photos yet, but it should go from the Neutral on the left of the brown cable to the securing screw in the Neutral bar above it?
No - it is the supply neutral to the RCCB - the other end will be wherever the power comes from, the same as the brown.
 
I would isolate that main supply, undo that terminal screw, and see if that brown might push a bit further into the terminal, before re-tightening.

I'm not impressed with the armoured cable, being installed without a proper gland.
 
Re-terminate the Live while you're at it, too much copper is showing.
I'd at least expect a stuffing gland to hold the cable in place
 
Neutral on the left of the brown cable to the securing screw in the Neutral bar above it?

Yes, well the neutral terminal, to the left of the brown/ the terminal, at the top of the RCD, with a moulded letter N, next to it.

Not the neutral bar!
 
Re-terminate the Live while you're at it, too much copper is showing.
I'd at least expect a stuffing gland to hold the cable in place
I'm more concerned about the outer sheath and armour being removed, the inner sheath is more of a filler not intended to be exposed outside of an enclosure.

Can we have a pic of that too?
 
Hi guys, many thanks for all your help it's appreciated;
I now know where to replace the disconnected cable but I think after reading all the comments on sheathing and glands, I should get an up to date electrician in to renew the complete cable from tne domestic box, and have it safe for the future.
Cheers and thanks to all.
 