Do regular circulating pumps have any "non return" ability?

Joined
7 Oct 2008
Messages
109
Reaction score
42
Location
Surrey
Country
United Kingdom
Currently working through the bodges in self and neighbours new build houses that were completed a five years ago. Developer and plumbers all gone bust and it was the plumbers first attempts at installing ASHP systems. There is a list of issues as long as your arm but one of them is in 2 of the 4 houses there are no NRVs on the HW circ pumps (Stuart Turner ST 15/60 B-130).

The plumbers didn't lag any HW pipes underfloor or in the equipment cupboards and left the pumps on the redundant CH channel of a standard heating/HW timer set to "ON". In the last week, I discovered the neighbours had their circ pumps on 24/7 for 5 years and wondered why their HW is never hot and why their bills are high (3 and 4 bed houses).

I'm going to add an NRV to my system but before I do, just wondered if this type of pump actually offered any resistance to reverse flow when it wasn't running. At the moment, I guess "out of hours" HW drain runs the hot water down two pipes to the taps. It's particularly bad in the kitchen where they buried the copper pipes under the floor or run them through unheated voids without any insulation on the pipes.

They were so gash, they couldn't even clip down the UFH pipes before screeding. Neighbour also has a W Plan set up where they put the 3 port valve in the wrong way so the CH/HW calling to the ASHP has never worked properly (he manually opens the valve).

Here's my kitchen floor.


pipes.jpg
 
No it's a centrifugal pump, water will pass through either way quite happily without restriction. Normally the return line would be plumbed into the cold main at the cylinder, so without a nrv you'll be drawing cold from the main with the hot when opening the hot tap
 
Thank you for that, I guess that's why it's called a circulator. There is a specific HW return connection on our unvented (ASHP supplied) cylinder but running the pump is still inefficient for us as only two in a 4 bed house with 6 hot taps (kitchen, 2 ensuite, bath, cloaks & utility) and the installing plumber never insulated any of the pipework. (What you see in this pic is my work). Circ pump top right of photo.

HW_ret.jpg
 
Nice job, I guess you're still kind of stuffed where it's run under the floor. Might be worth putting it on a timer so it's ready for the morning uses, maybe after tea etc.
 
Nice job, I guess you're still kind of stuffed where it's run under the floor. Might be worth putting it on a timer so it's ready for the morning uses, maybe after tea etc.
I've already got a timer (I use a Heatmiser Neoplug so it integrates with their app which runs my heating).

Rather than run the circ pump for longer than we need, I was thinking of adding the NRV so that running the kitchen tap, for example, isn't pulling hot water through the two HW pipes (flow and return) when the pump is off thus doubling my energy losses for the sake of a £7 bit of plumbing.
 
Something I hadn't tried before (stupid me) was to try to draw hot water with the main HW feed at the top of the cylinder turned off (red handle visible in pic above). We have about 2.5 bar of water pressure yet no hot water came out of any hot tap in the house as soon as the main stop was off.

This indicates there must already be a NRV in that return line somewhere. Knowing the standard of plumbing here, it's probably under a glued down chipboard floor somewhere between the pump (on the return line) and the first tap it goes to.

So, apologies to the plumbers, you did fit one, but where?
 
Could you have lagged it without realising? Not an issue til it stops working anyway - I will say the pipework seems relatively tidy from what I can tell.
 
Could you have lagged it without realising? Not an issue til it stops working anyway - I will say the pipework seems relatively tidy from what I can tell.

No, don't think so as I identified and labelled everything in that cupboard whilst I put the insulation on.
 
Poorly done secondary returns totally kill the COP of heat pumps plus the heating is compromised.

I would do away with the timeclock and run it on pirs set above the doors so when you walk into a bathroom the pump runs for 30 seconds or so
 