Does it matter if boiler is slightly over sized?

Discussion in 'Plumbing and Central Heating' started by benaround3, 4 Apr 2012.

  1. benaround3

    benaround3

    Joined:
    15 Apr 2007
    Messages:
    26
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    Thank you for pointing me to that.I am using the below, which may be different as it is described as "compact". It says that the boilers modulate down by a third, which may apply to the bigger ones as well, so they may not all go down to the same value.

    http://www.viessmann.co.uk/etc/medi...e.Par.12469.File.File.tmp/DPGOCT2011_web1.pdf
     
  2. benaround3

    benaround3

    Joined:
    15 Apr 2007
    Messages:
    26
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    Are you saying the Intergas has an advantage? If so I will go for it. How do I get an in-line stat? Will my Heating Engineer fit this or does the Intergas have one? I am thinking of an OV by the way.
     
  3. MJN

    MJN

    Joined:
    30 Apr 2008
    Messages:
    549
    Thanks Received:
    63
    Location:
    Wiltshire
    Country:
    United Kingdom
    It only applies to the big one.

    They do - the MI's say so (and are more likely to be correct than the marketing material).

    Mathew
     
    • Thanks Thanks x 1
  4. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    59,649
    Thanks Received:
    3,070
    Location:
    21st Century
    Country:
    Cook Islands
    Ah, the "compact" is the non-combi one which you use with a cylinder, I got one of those because it is simpler and has less to go wrong.

    It will occasionally run at full power if I have been away, when it is heating the rads from cold, or in cold weather when it is heating a cylinder of very cold water, then it modulates down as the heat requirement eases off.

    I used to work away a lot, so have oversized rads which with an oversized boiler can heat the house faster from cold.
     
  5. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    See your other thread.

    Having the sensors in the block means it can and does condense even for hot water.
     
  6. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,400
    Thanks Received:
    1,300
    Location:
    Kent
    Country:
    United Kingdom
    I can vouch for that. When I left school - many years ago - I went to work for a company within the Philips group. I learnt that TVs were made on a single production line and then tested to a high standard. Those which passed were put into cases with a Philips badge one the front. The failures were then re-tested to a lower standard, if they passed they went into a case with another name on it (I think it was Sobell). Failures were sent back for rectification.

    The same happened on the semiconductor production line - different batches from the same production line would be given different type labels depending on the results of the quality control tests.
     
  7. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,042
    Thanks Received:
    9,421
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Exactly what Intel and AMD do with their processors.

    Car manufacturers do the same as well. They are catering for different corners of the same market.
     
  8. benaround3

    benaround3

    Joined:
    15 Apr 2007
    Messages:
    26
    Thanks Received:
    0
    Location:
    Hampshire
    Country:
    United Kingdom
    Thanks but you have gone a bit fast for me. Is the "sensor in the block" the same as an in line stat? If it is then I think I get it. Something integral with the boiler that measures the water temp as opposed to the air temp can ensure the boiler is only on when the water is cold enough to allow condensation mode. I did look at my other thread but it didn't help.
     
  9. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    No the inline stat is different. One would need to make something up with whats available.

    The room stat/ compensation controls the room temperature, you need a simple stat, that makes on temperature fall like a frost stat, in the heating return pipe.

    What it means is the return can never go above a set temperature.

    I would have thought Alec would be the best guy.
     
    • Thanks Thanks x 1
  10. ALEC1

    ALEC1

    Joined:
    21 Nov 2009
    Messages:
    9,496
    Thanks Received:
    717
    Location:
    London
    Country:
    United Kingdom

    My point entirely is that the search for the low end modulation is misplaced..as boilers with compensation controls deal with the lowend very well any way. Correctly sizing boilers is the key, and with a house with a 4.2 kw boiler perhaps another fuel should be used...
     
  11. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,560
    Thanks Received:
    4,511
    Location:
    London
    Country:
    United Kingdom
    The ONLY extra component their combi has is the DHW flow switch!

    Apart from the DHW pipe!

    Tony
     
  12. peekay53

    peekay53

    Joined:
    22 May 2011
    Messages:
    668
    Thanks Received:
    95
    Location:
    Merseyside
    Country:
    United Kingdom
    for the house you have described i myself would fit a intergas combi range rated down to minimum for heating remember intergas are condensing in hot water mode also and ideally when a boiler is condensing it is running effiently just my opinion and sure someone will try to shoot me down well good luck in your search
    peekay53
     
  13. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    59,649
    Thanks Received:
    3,070
    Location:
    21st Century
    Country:
    Cook Islands
    What, no heat exchanger and no pressure vessel? no pressure gauge and no filling loop? No aquablock? No internal pump? No diverter valve?
     
  14. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,400
    Thanks Received:
    1,300
    Location:
    Kent
    Country:
    United Kingdom
    The only way any boiler can deal with a heat requirement which is below the low end is by reverting to on-off mode. This automatically reduces the efficiency of the boiler, mainly due to the effect of the start up routine the boiler goes through each time it lights. The smaller the ON time, the greater the reduction in efficiency.
     
  15. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,560
    Thanks Received:
    4,511
    Location:
    London
    Country:
    United Kingdom
    Most boilers lose heat when the burner is off and this inefficient.

    The Intergas HE has considerable latent heat and I suspect it may be more efficient than other types when forced into on/off modulation.
     