Yes, that's what I said I would replace it with. Plus a circulator pump I think.it still needs a thermostatic valve
misunderstood your post.
Yes make your own if it just has one circuit, thats what i plan to do for my lounge at home, but of course it wont have flow meters and thermostat pockets etc built in
What size area are you trying to heat?
Danfoss supply three types of return temperature limiter for underfloor heating.
The FHV-R used in systems predominately heated by radiators.The FHV-A used in systems where low flow temperatures are available from mixing valves or boilers set to low flow temperatures where individual room control is required without the use of electrical equipment.
And finally the FJVR used in systems where several rooms are heated by UFH with one valve fitted per loop and where the rest of the system is heated by radiators.
The flow temperature from the boiler may well be above 70c which is too high. Screed damage may occur if you allow this to flow through the loop unchecked and aside from that you don't need your feet cooked up like kippers.
The floor surface temperature required is usually quite low and very close to the actual room temperature.
It should be at or below 29c in all occupied areas so as to acheive an acceptable degree of foot comfort.
Lower temperature limits are sometimes required for timber floors.