    Hi,

    I've just had an old garage roof taken off, and i've just been running some new armoured cable to replace the old standard twin and earth that used to feed that building (surprisingly wasn't in very good shape!).

    The roofers cut off the old twin and earth when they removing the old roof, no problem. But I've also spotted an yellow/green earth cable that's been cut off as well that runs into next door's outbuilding. There's no sign of where it ran to my end, if anywhere.

    After looking in next door, it runs into a mini consumer unit. A small loop of earth cable then runs out of the unit and clamps round the exposed armour of the main feed into that unit.

    My question is, should the earth cable that has been cut of be providing an earth for that consumer unit, and therefore all the circuits that run from it? Or may it have been there to earth something which might not even exist any more?

    If it should be earthing the CU, can I just connect it to a new earthing rod?

    Many thanks!
     

    Attached Files:

  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,363
    Thanks Received:
    1,308
    Country:
    United Kingdom
    Next door's CU feed runs through your garage??
     
  4. robinbetts

    robinbetts

    Joined:
    3 Feb 2008
    Messages:
    20
    Thanks Received:
    0
    Location:
    Cardiff
    Country:
    United Kingdom
    It's just their outbuilding, and it's just this earthing cable that runs along the top of our boundary wall, and it was tacked onto the side of the wall plate of my old garage roof. My garage backs onto their main building, so it's possible that the earth cable used to go in there somewhere. But theirs no sign of it that I can see!
     
  5. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,469
    Thanks Received:
    919
    Location:
    Essex
    Country:
    United Kingdom
    Id suggest your neighbour gets there earth tested to there garage cu, its possible whoever installed there swa did not terminate the armoured at the house end, either through incompetance or purposely chose not to and TT'd the garage, the cable may have gone to an earth rod.
    Can they check there end in the house to see how the swa connects
    If they turn out to need a earth rod it needs installing correctly and on there property really.
     
  6. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,965
    Thanks Received:
    1,782
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have seen, specially around radio hams, where out building had a TT supply and that also included their neighbour. It was more to do with RF interference than safety from electric shock, but first thing would be ask your neighbour.
     
  7. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
  8. Sponsored Links
  9. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    It's not your CU - do not have anything to do with it, particularly providing an earth.

    Tell them that their earth was running through your roof and therefore, unfortunately, it has been severed.

    Advise them to get an electrician to sort it out, and in the meantime isolate the supply to their outbuilding.
     
  10. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,410
    Thanks Received:
    887
    Country:
    United Kingdom
    Presumably that earth cable is to parallel the swa shield to allow enough CSA? But the electrician didn't know what he/she was doing as they have used an earth clamp for a copper pipe which is not suitable for SWA. So they need an electrician anyway to sort that out, and while they're there they can check the earthing arrangement.
     
  11. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    You forgot something:
    ;)
     
  12. robinbetts

    robinbetts

    Joined:
    3 Feb 2008
    Messages:
    20
    Thanks Received:
    0
    Location:
    Cardiff
    Country:
    United Kingdom
    Thanks guys,

    I'm on good terms with my neighbour who is elderly, so don't really want to cut her cable then say "you sort it out" or "it's nothing to do with me" so I'll do what I can to help her get it sorted and put right if necessary.

    I assume that the correct way to earth bond the swa is to use a gland kit and attach the earth to the tag?

    Thanks again.
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,841
    Thanks Received:
    4,261
    Location:
    Retired to:
    Country:
    Portugal
    Perhaps ALL of next door's supply comes from yours.

    Are your bills high? :)
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    You don't have to - it's already been cut:



    Or an earthing nut.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page