SparkyTris said:
Following on from this: the distribution of electricity to a residential street applies adjacent phases to adjacent properties. (correct me if I'm wrong!)
Well, the houses aren't always connected in strict A-B-C-A-B-C sequence along the street, but you have grasped the principle that the services will be as evenly balanced as possible between the three phases.
Therefore at least occasionally, very large currents (up to 3 x highest phase current) would flow in the neutral line. But the neutral conductor out in the street has the same Cross-sectional area as the phase conductors.
You're making the mistake of just adding the individual phase currents together and assuming that the total must be the neutral current. You can't use a direct arithmetical sum of the phase currents because there is a 120 degree difference in phase between them.
If the three live lines were all in phase (i.e. the black, red, and blue waveforms above were shifted so that they were on top of each other), then the neutral current would indeed be the sum of the individual phase currents. But as soon as you move the phases apart, that is no longer the case.
Three-phase can be quite complex to understand at first, but an easier way to start getting an understanding of this is to examine the simpler single-phase 3-wire system. This is widespread in North America, but also found in rural areas of Britain.
The 3-wire arrangement has a neutral plus two live lines, which are 180 degrees out of phase with each other. (Imagine two waveforms like those above, arranged so that the zero-point coincides but such that when one is at peak positive the other is at peak negative. We'll c all these A and B.)
Now, assume a load of 15A connected on the A side to neutral. At this point, with nothing on B, you would have 15 amps flowing on the A line and obviously that 15 amps must also flow along the neutral.
Now let's say you connect a load of 5A between B and neutral. Obviously the current in B is now 5 amps, but what happens at the common neutral point? If A and B were in phase, then the currents would add, resulting in 20A. But A and B are 180 degrees out of phase. When A is positive, B is negative, and vice versa (or if you like, when one side is pushing the other is pulling, if that helps you to visualize it better).
If you have 15 amps flowing toward the neutral point from A, but at the same time you have 5 amps flowing away from it via B, then the neutral current is the difference: In = Ia - Ib = 15 - 5 = 10 amps. If the loads on A and B are identical, then Ia = Ib and therefore the neutral current drops to zero. In this 3-wire system, the neutral current can
never exceed A or B, whichever is the greater.
Once you can picture what is going on with this simpler system, you can then make the step up to 3-phase where it is more complex. With a 3-phase system, when the same current flows on A, B, and C, the neutral current drops to zero.