Need some experience on this please. I'm a maintenance engineer in a food factory. Our site services engineer asked me to check a cable as he got an electric shock from it.
Mains switchroom with 4 incoming transformer supplies. He isolated a supply feeding a compressor to remove cable as was to supply a new bit of kit. When he unbolted the old cables he didnt get a shock, panel was switched off and he checked for dead. When he pulled the cables out of panel, the neutral got jammed so he pushed the cable lug and got a belt. When he asked me to check, I checked line to line 0v, phase voltage again 0v. Cables were just dangling in the isolated cabinet. I checked the neutral to earth voltage and got 230v. Which is why he got zapped. We went to the other end of the cable, next room in switchroom and turned off the isolator, again 230v neutral to earth. I took out the neutral link out from this end, so both ends of supply cable now isolated from anything else. 0v neutral to earth. So mains incomer cable ok. Connected test meter to machine neutral otherside of neutral link and 230v to earth. So neutral is getting a 230v from somewhere. This is where I'm stuck as not my area of expertise. Not going to be my job to rectify as its not my work department. Any ideas on what is causing this issue. The 4 incoming transformers are in a locked area on otherside of incoming switchroom. These then feed other areas of factory distribution. Would a transformer neutral to earth connection cause this fault. How is an isolated 3 phase machine getting 230v neutral to earth? Tia