A machine in work has been intermittantly stopping, and when conducting some tests today I found a voltage between neutral and earth of around 100Volts (cant be 100% on the accuracy of these values as it was late, and I didnt write them down).
When I tested phase to neutral I got
L1 - N 360Volts
L2 - N 120Volts
L3 - N 360Volts
Phase to earth values
L1 - E 240Volts
L2 - E 240Volts
L3 - E 240Volts
And phase to phase values were all around 420Volts.
Any opinions on what could be causing this?
Some sort of L2 - N fault?
An imbalance in the phase loads?
Loose neutral connections somewhere?
When I tested phase to neutral I got
L1 - N 360Volts
L2 - N 120Volts
L3 - N 360Volts
Phase to earth values
L1 - E 240Volts
L2 - E 240Volts
L3 - E 240Volts
And phase to phase values were all around 420Volts.
Any opinions on what could be causing this?
Some sort of L2 - N fault?
An imbalance in the phase loads?
Loose neutral connections somewhere?