I was asked to have a look at an electrical installation recently:
there is a "normal" PME 240VAC supply feeding a medium sized solid-state 3-phase 400VAC generator (based on VFD inverter I think)
this machine outputs 3 conductors L1 L2 L3, being the three phases; 415VAC interphase.
as an afterthought, a "neutral generator" (not my words) has been installed.
this is a machine in a vented steel case into which the three phase lines are connected, and out of which comes a Neutral line. I believe there is a transformer inside this steel case.
there is 240VAC from each phase to this neutral conductor. (which is what the so-called neutral generator was installed for)
there is 160VAC between the incoming PME 240VAC neutral and the abovementioned 3-phase "synthesised neutral".
Why is there a significant voltage difference between the incoming DNO neutral and the 3-phase neutral?
there is a "normal" PME 240VAC supply feeding a medium sized solid-state 3-phase 400VAC generator (based on VFD inverter I think)
this machine outputs 3 conductors L1 L2 L3, being the three phases; 415VAC interphase.
as an afterthought, a "neutral generator" (not my words) has been installed.
this is a machine in a vented steel case into which the three phase lines are connected, and out of which comes a Neutral line. I believe there is a transformer inside this steel case.
there is 240VAC from each phase to this neutral conductor. (which is what the so-called neutral generator was installed for)
there is 160VAC between the incoming PME 240VAC neutral and the abovementioned 3-phase "synthesised neutral".
Why is there a significant voltage difference between the incoming DNO neutral and the 3-phase neutral?