Is this a TN-S do you think.
It does, and if it were TN-C-S, one would expect to see a 'PME sticker'.It looks like TN ...
If the installation's earth is derived from a separate conductor (i.e. the sheath of the incoming cable) then it is TN-S, regardless of what connections there are between neutral and earth outside of the installation (and, after all, there has to be at least one such connection, at the transformer). The installation is TN-C-S only if the installation's earth is derived from the neutral of the incoming supply cable.... however only the DNO can say if TN-S or TN-C-S as only they know is some where along the supply root is the earth and neutral have been combined or not.
I don't have latest version of BS7671, I am still on 2008 version, however that version if anywhere between the step down transformer installation and the premises the earth and neutral are combined it is classed as TN-C-S as the risks are the same, i.e. if the combined earth neutral is lost the earth can rise in voltage, so use of TN-C-S is banned for petrol stations, caravan parks, boat marinas etc.It does, and if it were TN-C-S, one would expect to see a 'PME sticker'.
If the installation's earth is derived from a separate conductor (i.e. the sheath of the incoming cable) then it is TN-S, regardless of what connections there are between neutral and earth outside of the installation (and, after all, there has to be at least one such connection, at the transformer). The installation is TN-C-S only if the installation's earth is derived from the neutral of the incoming supply cable.
Kind Regards, John
There's also a Brass connector block sticking out to the right of the Neutral with an Earth connected going to the MET, Perhaps the DNO just wanted people to guessIt looks like TT. You can see that that g/y is taped to the sheath of the supply cable, and is heading off somewhere - to an earth rod?
I'll have to look to see what BS7671 says, but what you say above makes no sense to me. If the installation's earth is derived from the sheath of the cable (i.e. TN-S), rather than from the incoming neutral, how on earth can 'loss of the neutral' have any influence on the potential of the installation's earth (unless there is yet another simultaneous network fault)? What am I missing?I don't have latest version of BS7671, I am still on 2008 version, however that version if anywhere between the step down transformer installation and the premises the earth and neutral are combined it is classed as TN-C-S as the risks are the same, i.e. if the combined earth neutral is lost the earth can rise in voltage ...
Exactly this does happen, I would guess with petrol stations, caravan parks and marinas the DNO must inform the customer if a TN-S is converted to TN-C-S however supply not covered with BS7671 so don't know the rules, but you can see from head if TT or TN and in some cases you can see when it's TN-C-S but you can never be sure it's TN-S unless the DNO tells you.I think Eric is saying that a section of cable under the street can get replaced with a section without an earth sheath, presumably because of the lack of availability of the other kind.
If that is true, and the installation's earth is connected to the sheath of the incoming cable, then the installation won't have an earth at all (except, maybe, a sort-of TT one if there is some of the sheath exposed to the earth/soil) - and there still wouldn't be any reason why the potential of that 'earth' (or non-earth) should be influenced by a neutral fault, is there?I think Eric is saying that a section of cable under the street can get replaced with a section without an earth sheath, presumably because of the lack of availability of the other kind.
yes, that happens. However, if it does, then the installation has to derive its earth from the neutral (not the cable sheath), and hence would be 'obviously TN-C-S.Exactly this does happen ...
That's a new one on me. Is it actually allowed to have a TN-C-S earth entering the building separate from the supply cable?Readings made me think TNCS but connection/separation must be under the pavement. Earthing conductor taped to the supply cable disappears in a hole in the basement wall, seemingly connected under the pavement...
If that is true, and the installation's earth is connected to the sheath of the incoming cable, then the installation won't have an earth at all (except, maybe, a sort-of TT one if there is some of the sheath exposed to the earth/soil) - and there still wouldn't be any reason why the potential of that 'earth' (or non-earth) should be influenced by a neutral fault, is there?
Kind Regards, John