It is.I thought it was 27A max with no correction factor.
That may be correct but then you have to protect the cable.Lamona says 2.5mm for the hob and 1.5mm for the oven.
You are looking at it the wrong way round. The hob only 'needs' 2.5mm² and the oven 1.5mm².I reckon the Hob need 4mm and the Oven needs 2.5mm,
No. that's a different matter. You must stick to the actual number.as with a 32A breaker and CCC of the 1.5mm cable of just 20A that would be a ratio of 1.6 and the max has to be 1.45 doesn't it?
You are looking at it the wrong way round. The hob only 'needs' 2.5mm² and the oven 1.5mm².I reckon the Hob need 4mm and the Oven needs 2.5mm,
Mistakes occur.I get your point, but the techical data in their booklet says "Fuse protection 32A" ... and two lines down ... "2.5mm 3 core" - these aren't even compatibale with each other???
That would be the best option. 4mm² flex isn't much bigger than 2.5.1. Wire both in 4mm (although it looks like I may be struggling with 4mm on the connection to the oven appliance, so this might not be possible)
No point but yes.2. Wire Hob in 4mm to the first CCU, and then ADD a 13A FCU from the from second CCU so I can then wire in 1.5mm from that FCU to the Oven.
As it's already there I would leave it. As you say, you can isolate it from above.TWO SUBSEQUENT QUESTIONS
A. If I add a FCU, since I can isolate both appliances from the cooker switch IS IT OK TO LOCATE THE FCU BEHIND THE OVEN OR SHOULD IT BE PLACED IN A CABINET?
You shouldn't but it doesn't apply (replace second ccu)B. Since the oven will be protected by a 13A fuse, can I use 2.5mm from the seconds CCU to the FCU?[/u]
No you must use 4mm² because it is on a 32A mcb.
Forget about the 1.45.
That is the fusing factor of the mcb and not to do with these circuit design calculations.
No, because there's a fuse in the plug which protects the flex.If what you are saying is right, doesn't that mean the flex of all kettles, toasters etc. plugged into a 32A ring must also be in 4mm, because in fault conditions the current will be way over the CCC of the flex?
Do you feel confident to do the necessary adiabatic calculations to show that flex that size will be adequately protected against faults by a 32A breaker?So provided that the flex is suitable for the aplliance, 2.5mm for 6.5kw and 1.5mm for 2kw is it OK to wire both onto the same cooker circuit isolated by a single cooker switch protected at the CU by 30A? ... or not