I was going to run the cable over and do all the main bits and get a spark in to connect it up as have a little unit in the garage hopefully fit an rcd
I was going to run the cable over and do all the main bits and get a spark in to connect it up as have a little unit in the garage hopefully fit an rcd
I was going to run the cable over and do all the main bits and get a spark in to connect it up as have a little unit in the garage hopefully fit an rcd
If so, your best option is to use one of those to power to the shed.
BUT
the 2.5mm² cable I specified is too small for a 32A supply. You have two options
1. Change the breaker for a 20amp one (must be a CPN one)
2. Use 4mm Cable. https://www.tlc-direct.co.uk/Products/NY4slash3.html
but this is really circuit design territory. You should be using an electrician to tell you exactly what your options are.
Are those two MCBs on left spare? If so, your best option is to use one of those to power to the shed. ... BUT ... You should be using an electrician to tell you exactly what your options are.
Indeed, and another 'BUT' (and another reason for engaging a 'self-certifying' electrician if one went down that route) is that, even though those MCBs are 'already there', I imagine that most people would say that connecting something (the first and only something) to them would constitute creating a 'new circuit' - hence notifiable.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local