    I'm going to have an EV charge point installed and have already been told there needs to be a separate earth rod if the charge point is outside. The charge point will be fed by the necessary RCD/RCBO/2-pole switch, etc and an underground SWA cable as the charge point will be on an outside wall about 5m from the house.
    As a point of interest, does the SWA armouring get earthed via the house earth (which is already via an earth rod due to being a non-PME system) or does it rely on the new earth rod near the charge point? Which earth takes on the cable earthing role? I get the feeling there may be some discussion over this with my electrician who hasn't seen the location of the charge point, etc, yet.
    Can anyone advise? Thanks.
  2. Sponsored Links
  3. EFLImpudence
    EFLImpudence
    7 Jul 2010
    37,452
    Thanks Received:
    4,199
    Retired to:
    Country:
    Portugal
    Usually for TN earthing systems the armour would be earthed at the origin and kept separate from the charging area if that were TT.
    As you already have a TT earthing system (rod) it could be connected at both ends.
    You are relying on RCDs for earth fault disconnection.
    I get the impression that no one really knows what is best yet.
    https://www.google.pt/webhp?sourcei...UTF-8#q=vehicle charging on already tt system
  4. securespark
    securespark
    11 Jan 2004
    37,142
    Thanks Received:
    1,288
    Country:
    I would use the earth from the house rod solely to connect the armour to, then use another rod local to the point to connect the external stuff to.
    You want to avoid a voltage gradient between the rods. You could also link the two rods I suppose.
  5. Tipper
    Tipper
    1 Dec 2008
    1,145
    Thanks Received:
    103
    Devon
    Country:
    Thanks guys so far.
    If the earthing arrangements are separated, ie, cable armour from supply point and charge point via new earth rod, then presumably there is no need for 3-core SWA (ie 'twin&earth') because the earth core would not be connected to anything and a two-core would suffice? (Not sure if this reduction in spec would actually reduce the cost significantly. Most of the cost I suspect will be cable route installation and trenching!)
  6. EFLImpudence
    EFLImpudence
    7 Jul 2010
    37,452
    Thanks Received:
    4,199
    Retired to:
    Country:
    Portugal
    Yes, two core would do. It may anyway if the armour were big enough for the earthing.
    Where is the present rod in relation to the charging point?
    As SS said "You could also link the two rods I suppose".
    By the armour?
  7. Tipper
    Tipper
    1 Dec 2008
    1,145
    Thanks Received:
    103
    Devon
    Country:
    The two earth rods would be either side of a double garage, say, 15-20m apart. The house consumer unit is in the garage about 3m from the house earth rod. The charge point supply cable would be about 15m long. The charge point earth rod would be directly below the charge point say 1m.
    Doesn't connecting the earth rods together cause a problem or is that when there are two earthing systems ie PME and a separate earth rod? Sorry my earthing knowledge is very rusty!
    I'll be getting my electrician involved shortly but I find the ins and outs of this really interesting. (y)
    (The house which is about 40 years old now was found to have no earth at all before it was rewired 2 years ago. It was a shambles electrically hence total rewire carried out including new earthing arrangements. The meter tails to the consumer unit were described as '10mm twin&earth cooker cable'. It is on a single phase O/H line with SWA final incoming cable across the garden from the last pole.)
  8. Sponsored Links
  9. ban-all-sheds
    ban-all-sheds
    27 Aug 2003
    69,782
    Thanks Received:
    2,858
    London
    Country:
    Or by 5m of this buried in the ground:
    [​IMG]
    The last time I checked the people linked to were considerably cheaper than anybody else.
  10. ericmark
    ericmark
    27 Jan 2008
    18,600
    Thanks Received:
    1,745
    Llanfair Caereinion, Nr Welshpool
    Country:
    You say your on TT so what is the problem? Only with TN is there a problem. With TT just link all earth electrodes together.
  11. Tipper
    Tipper
    1 Dec 2008
    1,145
    Thanks Received:
    103
    Devon
    Country:
    That's what I had assumed but was looking for confirmation. Thanks.
  12. securespark
    securespark
    11 Jan 2004
    37,142
    Thanks Received:
    1,288
    Country:
    If the CSA is sufficient, why not?
    Although the extra cost of a copper conductor over that distance would not be significant.
  13. EFLImpudence
    EFLImpudence
    7 Jul 2010
    37,452
    Thanks Received:
    4,199
    Retired to:
    Country:
    Portugal
    Yes, but you said:
    but:
    by the armour?
  14. securespark
    securespark
    11 Jan 2004
    37,142
    Thanks Received:
    1,288
    Country:
    Yeah. Senior moment. Dozy wazzock. I am 50 in three months time...
    Thanks for pulling that up!
    I was thinking TN at first, then thinking about linking the rods together to avoid a voltage gradient. There would not be two rods if it were a TN system...