Electrical appliances near boilers

Joined
21 Aug 2013
Messages
1
Reaction score
0
Location
London
Country
United Kingdom
Hi there

I have a Vailant EcoTEC (about 4 years old) in a cupboard measuring roughly 1.5m wide x 1m deep x 3.5m. Plenty of space around it, and it was fitted into that cupboard a year ago by a Gas Safe registered fitter.

I'd like to put a small freezer in the bottom of the cupboard, but can't find any info online as to whether this is permissible or accepted practice.

Can anyone offer any advice?

Cheers

Bob
 
Sponsored Links
I don't think you should have any problems with regards to regulations/requirements to this.
But there is a gas regulation concerning the proximity between electrical fixtures (meters, switches, sockets, distribution boards etc...) and the gas meter/pipes.
*no less than 150mm separation.
Also the separation of electrical cable and flex, should be at least 25mm from gas pipe up to 35mm dia or 50mm if greater.

So I suggest you keep to those and obviously any pipes supplying heating/hot water should also be offered separation.
 