Fellas,
Still learning my way regarding fault finding, wondering if anybody can see any flaws or would they do it a different way with a slight problem today.
Split load board, 3 ring mains and a shower on RCD side, its a clipsall CU and i noted it was a terrible install.
RCD trips out about 5 times a day, the lady said it could be any appliance at all that trips it.
I isolated the ringmains and turned one on at a time checking each appliance as i went along, everything was fine on all the ring mains and shower.
I then plugged rcd tester in 1 ringmain and applied half the current, it tripped.
I then turned this ringmain off and did the same test on another ringmain and it tripped at half the current.
I then went to board, (test button on rcd was a bit dodgy) and applied the 3probes to load side of rcd, tripped out at half the current, im assuming its a faulty rcd (button was knackered anyway so needs replacing regardless)
Any advice appreciated?
Still learning my way regarding fault finding, wondering if anybody can see any flaws or would they do it a different way with a slight problem today.
Split load board, 3 ring mains and a shower on RCD side, its a clipsall CU and i noted it was a terrible install.
RCD trips out about 5 times a day, the lady said it could be any appliance at all that trips it.
I isolated the ringmains and turned one on at a time checking each appliance as i went along, everything was fine on all the ring mains and shower.
I then plugged rcd tester in 1 ringmain and applied half the current, it tripped.
I then turned this ringmain off and did the same test on another ringmain and it tripped at half the current.
I then went to board, (test button on rcd was a bit dodgy) and applied the 3probes to load side of rcd, tripped out at half the current, im assuming its a faulty rcd (button was knackered anyway so needs replacing regardless)
Any advice appreciated?