I plan to fit 2 smoke alarms. Can i wire them into 16A MCB which is not on the side of the RCD? Is it ok just to use 2.5mm twin and earth? I plan to wire them both off the 16A MCB on a radial circuit.

cheers for help
 
Sponsored Links
.put them on the non rcd side on a 6amp.you will need 1.5 cable max because you will never get 2 2.5 cables in the terminals of the first one.also you will need to interlink the first to the second.you cant do this if you only got two cores
 
depends if the op has interlinkable smoke detectors though
 