I'm having an extension built where there was previously a brick bay. For whatever reason (I assume the builder didn't trust the foundation) he has used a floor beam as a lintel to span the bay and then rested the ends of the beam & block floor beams on it.

So effectively I have a 175x75 beam used as a 3m lintel for a domestic floor load.

I calculate the load as 19kN
4.2kN /m2 x 1.5m (half floor span) x 3m
The 4.2kN comes from Bison flooring spec guide.

What do you think, is that ok? Floor is bouncing but I know that's normal before grouting.

Thanks
 
Last edited:
Sponsored Links
I've found a load table for PCC lintels which says 140x100 is good for 3kN/m at a 3000 span which makes me think it won't be ok for 6kN/m at a 3m span?
 