• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Floor beam as lintel

bsr

Joined
5 Aug 2008
Messages
1,029
Reaction score
113
Location
Gloucestershire
Country
United Kingdom
I'm having an extension built where there was previously a brick bay. For whatever reason (I assume the builder didn't trust the foundation) he has used a floor beam as a lintel to span the bay and then rested the ends of the beam & block floor beams on it.

So effectively I have a 175x75 beam used as a 3m lintel for a domestic floor load.

I calculate the load as 19kN
4.2kN /m2 x 1.5m (half floor span) x 3m
The 4.2kN comes from Bison flooring spec guide.

What do you think, is that ok? Floor is bouncing but I know that's normal before grouting.

Thanks
 
Last edited:
I've found a load table for PCC lintels which says 140x100 is good for 3kN/m at a 3000 span which makes me think it won't be ok for 6kN/m at a 3m span?
 
Last edited:

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top