Garage submain - compact switch-fuse inside meter cabinet or metal-clad unit?

Proteus box is for the solar inverter, its not that its untidy, its just at the front of the house and looks fugly. I now have a "service corridor" inside the house, along the main soil stack so can route the cable through there and the outside wall and into the garage when I get the ducting buried under the driveway sometime next year which will mean there wont be any ugly cables clipped anywhere and I could get rid of the Proteus then, and move the inverter rcbo and the generation meter to the garage, just need to figure out upstream cable protection without ugly arse cables and boxes everywhere.
I've just bricked up the garage door so future me can also get a heat pump there so kinda makes sense to move these to the garage submain, its just going to be much tidier that way.
I'll do the earthwork and have a sparky connect it all when the ducting is ready(still need to figure that bit out with the access points, etc).
Fair enough, you're unlikely to need a 16mm cable for a garage unless you're planning on a hot tub out there.

Only 'weatherproof' with the cover closed.

Open it and whatever is inside is exposed to the external environment with all the dirt and humidity that exists.
Even with it closed, they will be subject to massive temperature variations which will lead to condensation.

Most MCBs and other similar devices used in domestic consumer units are rated PD2, for use indoors.
While PD3 and PD4 rated devices can be had, they are intended for use in industrial distribution boards.
These units are sold prepopulated with consumer grade mcbs/rcds.

I'd never heard about pollution degree, on googling this is what professional electrician has to say -

circuit- breakers to BS EN 60898 must be used in domestic settings.

While this standard is based on PD2 conditions (where only non-conductive pollution occurs), it does acknowledge that temporary conductivity, such as that caused by condensation, may occasionally be expected.

Therefore, installers should not be concerned about using BS EN 60898 circuit-breakers in outdoor enclosures, provided the manufacturer has tested and validated the assembly arrangement as suitable for such use.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top