Terraced house, edwardian, TNS, row of similar houses.
Building a shed/garden studio in the rear garden.
Intend to fit an RCD protected CU in the ched, supplying-
power sockets inside on a 16A series circuit (not a ring)
If possible, would also like to supply
underfloor heating 16A
power socets outside shed 16A
shed lighting 6A
So a five way CU, max demand I’m setting at a generous 32A
Supplied via three core SWA XLPE buried in the garden and then run down the entry and around the side of the house on cable cleats, into the front vestibule of the house through the timber surround of the window above the front door and into an isolator, then into the house CU which is in the vestibule. Planning to feed it from a 32A mcb (rcd protected) at the house CU.
Planning to use the house earth, will earth the armouring, bury the cable at 500mm etc.
Cable needed is approx 42m, maybe a bit less, will measure accurately shortly.
Comments are very welcome- I know it is notifiable work and I’ll need an electrician to supervise and test/inspect/ issue installation cert. If there is anyone who would be interested to do this (for a fee of course) I’d be very grateful.
Query- what surface to mount the CU on at the shed? does plasterboard qualify as non combustible? what else might? MDF?
Query- Any reason I can't use 4mm SWA?
Query- I bury the cable with tape, in a bed of sand- is any further protection where it emerges from the ground or otherwise needed, cable tiles aren't a requirement anymore are they? I’m worried about the short run up from the ground into the shed, imagining rats knawing on it.
Query- I could possible fit an earth rod too, I am thinking that will help if I run into Zs problems, with my lighting circuit plans particularly, would like to put it all in without an earth rod then fit one if I need too. Any comments are very welcome.
Thanks very much to everyone.
Building a shed/garden studio in the rear garden.
Intend to fit an RCD protected CU in the ched, supplying-
power sockets inside on a 16A series circuit (not a ring)
If possible, would also like to supply
underfloor heating 16A
power socets outside shed 16A
shed lighting 6A
So a five way CU, max demand I’m setting at a generous 32A
Supplied via three core SWA XLPE buried in the garden and then run down the entry and around the side of the house on cable cleats, into the front vestibule of the house through the timber surround of the window above the front door and into an isolator, then into the house CU which is in the vestibule. Planning to feed it from a 32A mcb (rcd protected) at the house CU.
Planning to use the house earth, will earth the armouring, bury the cable at 500mm etc.
Cable needed is approx 42m, maybe a bit less, will measure accurately shortly.
Comments are very welcome- I know it is notifiable work and I’ll need an electrician to supervise and test/inspect/ issue installation cert. If there is anyone who would be interested to do this (for a fee of course) I’d be very grateful.
Query- what surface to mount the CU on at the shed? does plasterboard qualify as non combustible? what else might? MDF?
Query- Any reason I can't use 4mm SWA?
Query- I bury the cable with tape, in a bed of sand- is any further protection where it emerges from the ground or otherwise needed, cable tiles aren't a requirement anymore are they? I’m worried about the short run up from the ground into the shed, imagining rats knawing on it.
Query- I could possible fit an earth rod too, I am thinking that will help if I run into Zs problems, with my lighting circuit plans particularly, would like to put it all in without an earth rod then fit one if I need too. Any comments are very welcome.
Thanks very much to everyone.