Gas rate differ on specific boilers

Joined
12 Jan 2009
Messages
13
Reaction score
0
Location
Edinburgh
Country
United Kingdom
Hi
I have been fitting vaillant 831 ecotec plus boilers for years now and have had no problem getting the gas rate required by always running 22mm gas pipe right to the boiler. I have done a couple of ferrolli 31kw boiler and have struggled to get the right gas rates? I am going to have to up to 1" pipe..has anyone else needed to do this. I am using no more bends and pipe than i have done on the vaillants.
 