I can't remember the location, but something in the back of my mind is saying that connecting the generator earth and the DNO earth is not permitted.
I'll try and check it
I'll try and check it
Interesting that it shows a local earth rod, but doesn't show the generator frame being earthed, or if/where N is tied to earth.Would this arrangement meet your needs?
Where does it say your not allowed to connect to DNO earth? You can't rely on their earth so have to have alternative methods of earthing but as far as I am aware there is no requirement to disconnect their earth.That's an interesting possibility.
Not allowed to put the earth through the C/O switch either, so not being allowed to connect to the DNO earth means either:
Would this arrangement meet your needs?
http://www.topgen.co.uk/connect-home.html[/QUOTE]
same piccy as the one I found ,this link has an FAQ
http://www.justgenerators.co.uk/pages/FAQ.htm
the diynot site has been down for the last hour or so for me ,anyone else having the same probs?
the diynot site has been down for the last hour or so for me ,anyone else having the same probs?
agreed and theres no reason why they shouldYou have to make provision for the fact that a DNO earth might be missing in the event of a powerloss but there is no requirement for generator earths and DNO earths to be kept seperate.
And if the supply uses cables with a PVC outer sheath and the service cable is cut under fault conditions, where is your earth now?
As I said I need to check but it is in an Electricity Supply Industry document that is referred to when approval is sought by a customer to connect a generator.
My supply is TN-S. But I expect that another right they reserve is to re-designate it TN-C-S when the connection back to the substation earth completely rots away.In general for TN-C-S they require that you do fit your own electrode as a means of referencing the system to earth, as they reserve the right to disconnect their neutral, and thus their earth without notice – especially during fault location.
Planned local earth for the generator is about 10m of 25x3mm tape.The recommend earth electrode resistance given in BS 7430 is 20 ohms and this might be difficult to achieve unless you have enough space to install multiple electrodes.
There will be a front end RCD.However, this figure is general and you might wish to argue that, if a front end RCD is employed, a higher value could be considered.
My thinking exactly.Remember power outages are relatively rare in urban areas at the moment – but who knows what the future will bring .
My preference would be for a diesel, one that I could run on a range of fuels.Small cheap petrol generators: are very noisy; produce dangerous fumes: and are not very reliable.