I recently looked at getting an EV charger installed and learned about PEN protection for the first time. I'm not an electrician so it wasn't something I'd previously thought about (also please forgive any misuse of terminology). To help get my head around it, I drew out a few pictures showing different fail scenarios. Curious if I'm missing anything.
It's a long post but if you have time to read over it and answer the questions relating to pictures 9 and 10, I'd be grateful.
1. Basic functioning system.
2. Neutral line failure:
3. Equipotential Zone protection:
4. Danger in non equipotential system:
5. Danger from simple current path to GND(?):
6. Limitted risk in Indoor setting:
7. Increased risk of path to GND in outdoor setting:
8. Risk of non-equipotential hazards enhanced outdoors:
Summary
PEN protection (where voltages of Live, Nuetral and Earth are monitored and all three disconnected during failure) is not a requirement for domestic, indoor electrical systems. This is because equipotential bonding and the generally high resitance to GND through floor coverings etc means, in the highly unlikely event of a neutral fail, occupants will be safe.
There's a definite grey area relating to outdoor 13A sockets in my opinion. Maybe it's different now but we had our house rewired 12 years ago and no PEN protection was aded ot the outdoor sockets fitted back then. I'm not 100% clear on why that is considered 'okay'.
PEN or PME fail protection is rightly mandated for EV chargers since the car is a large metal object which would provide a terrific opportunity for an electric shock either via damp ground or where the user touched the car and another earthed object at the same tinme. The length of time cars are left on charge also increases the likelyhood of their being connected during a supply failure event.
PEN or PME protection seems also to be mandated for high current (comando) style outdoor sockets. It's not clear to me why they should be considered a greater risk than a standard 13A outdoor socket (as illustrated above, the RCBO won't protect you either way) but I guess it may just be down to typical use cases for this type of socket (used to run larger, semi permanent installs of equipment).
Questions. I think the above pictures broadly lay out the risks associated with a PME failure but I have a couple of qurestions related to EV or other 'in garage' install and how earth bonding might actually afford greater protection here.
9. EV charging in garage. Why is it safer (apparetly does not require PEN protect):
10. Does earth bonding to metal water or gas main increase saftey of system betond ensuring equipotential of exposed metal pipework?
It's a long post but if you have time to read over it and answer the questions relating to pictures 9 and 10, I'd be grateful.
1. Basic functioning system.
2. Neutral line failure:
3. Equipotential Zone protection:
4. Danger in non equipotential system:
5. Danger from simple current path to GND(?):
6. Limitted risk in Indoor setting:
7. Increased risk of path to GND in outdoor setting:
8. Risk of non-equipotential hazards enhanced outdoors:
Summary
PEN protection (where voltages of Live, Nuetral and Earth are monitored and all three disconnected during failure) is not a requirement for domestic, indoor electrical systems. This is because equipotential bonding and the generally high resitance to GND through floor coverings etc means, in the highly unlikely event of a neutral fail, occupants will be safe.
There's a definite grey area relating to outdoor 13A sockets in my opinion. Maybe it's different now but we had our house rewired 12 years ago and no PEN protection was aded ot the outdoor sockets fitted back then. I'm not 100% clear on why that is considered 'okay'.
PEN or PME fail protection is rightly mandated for EV chargers since the car is a large metal object which would provide a terrific opportunity for an electric shock either via damp ground or where the user touched the car and another earthed object at the same tinme. The length of time cars are left on charge also increases the likelyhood of their being connected during a supply failure event.
PEN or PME protection seems also to be mandated for high current (comando) style outdoor sockets. It's not clear to me why they should be considered a greater risk than a standard 13A outdoor socket (as illustrated above, the RCBO won't protect you either way) but I guess it may just be down to typical use cases for this type of socket (used to run larger, semi permanent installs of equipment).
Questions. I think the above pictures broadly lay out the risks associated with a PME failure but I have a couple of qurestions related to EV or other 'in garage' install and how earth bonding might actually afford greater protection here.
9. EV charging in garage. Why is it safer (apparetly does not require PEN protect):
10. Does earth bonding to metal water or gas main increase saftey of system betond ensuring equipotential of exposed metal pipework?