I have a floor standing Gloworm 45-60 boiler which keeps going out. it can stay lit for hours and works fine when it is lit. it seems to go out around peak usage of gas 7-9 am lunch time and early evening. Could it be the gas regulator that is causing the problem. any clues
 
Thanks for that but the thermocouple has been changed a number of times, twice in the same day on one occaision but the problem still remains. I didn't have this problem during the summer when the boiler was just heating water and no CH was on.
 
Partially blocked pilot injector or defective power unit.

When was the appliance last serviced?

Dave
 