any body out there got any sujestions
went out to a gloworm compleatheat 55 been stood dormant empty property.
fan was jammed so so cleaned out and serviced boiler replacing fan .
great boiler fired up sweet as a nut,well at least long enough for me to finish setting gas rate etc and re fitting casing,
then boiler shuts down and would not start again,not without me keep powering up and switching off power. the boiler would then fire up run a while then, to same senario as soon as it shuts down, it will not relight, only the 1st two leds light on the pcb board at this stage the third led is not lit, which is aps fan prooved.
the aps appears to be working fine from comm to no to nc as per should be, further investigation found no voltage to aps.
if i apply a 240v supply to aps for a split second the boiler will start fan prove aps prove pilot and pcb and light. but on pausing just goes back to same as above, suspected pcb so rang gloworm after giving my life story and corgi no, they said pcb, iam always weary of technical as most always say pcb,as we all well know, but upon having took their advice well they made the thing. fitted new pcb, yes youve guessed it same problem further head scratching and investigation found if i remove the grey cover just below black solinoid and gently ease the brass cantilever on the gas valve, power is restored to boiler then same sequence as previous.
iam not one to keep throwing bits on so cautios of replacing gas valve any advice from other engineers would be nice thanks. both solinoids have 240v when boiler doing as it should,rang gloworm they said the board fitted must be faulty
as it was a replacement part no supplier (reputable) ordered guenuine part. only difference on this board is the wiring lable glued to front still same fault
oh by the way the fan was ceased solid and not an impulse diagnosis of problem.pcb on the other hand was gloworms doing lucy for land lord he is a freind of mine with a letting agency of his own so board can go back on my van untill needed any one else might have fleeced him or found the problem
ps sorry if i have gone on a bit
went out to a gloworm compleatheat 55 been stood dormant empty property.
fan was jammed so so cleaned out and serviced boiler replacing fan .
great boiler fired up sweet as a nut,well at least long enough for me to finish setting gas rate etc and re fitting casing,
then boiler shuts down and would not start again,not without me keep powering up and switching off power. the boiler would then fire up run a while then, to same senario as soon as it shuts down, it will not relight, only the 1st two leds light on the pcb board at this stage the third led is not lit, which is aps fan prooved.
the aps appears to be working fine from comm to no to nc as per should be, further investigation found no voltage to aps.
if i apply a 240v supply to aps for a split second the boiler will start fan prove aps prove pilot and pcb and light. but on pausing just goes back to same as above, suspected pcb so rang gloworm after giving my life story and corgi no, they said pcb, iam always weary of technical as most always say pcb,as we all well know, but upon having took their advice well they made the thing. fitted new pcb, yes youve guessed it same problem further head scratching and investigation found if i remove the grey cover just below black solinoid and gently ease the brass cantilever on the gas valve, power is restored to boiler then same sequence as previous.
iam not one to keep throwing bits on so cautios of replacing gas valve any advice from other engineers would be nice thanks. both solinoids have 240v when boiler doing as it should,rang gloworm they said the board fitted must be faulty
as it was a replacement part no supplier (reputable) ordered guenuine part. only difference on this board is the wiring lable glued to front still same fault
oh by the way the fan was ceased solid and not an impulse diagnosis of problem.pcb on the other hand was gloworms doing lucy for land lord he is a freind of mine with a letting agency of his own so board can go back on my van untill needed any one else might have fleeced him or found the problem
ps sorry if i have gone on a bit