Glowworm royale 240/6 ventilation

Joined
24 Jul 2008
Messages
251
Reaction score
15
Country
United Kingdom
Hello, I have a glow worm royale 240/6. I was not there at last years service but the British gas engineer said the ventilation was not enough and it will not meet the new regulation.

The size of the vent is 27cm by 17cm and is fitted to boxed section that the pipes run up to the loft are in for the back boiler. This vent is about 1 metre away from one of the outside vents. The vent on the outside I think is roughly about 20cm by 15cm.

I can feel the air coming through the inside vent. If I lift the hatch where the motorized valves live I can really feel the breeze.

I can’t see how it’s not enough since before the vent was move to the wall (that was about 5 yrs ago) it was originally on the floor on the other side of the fireplace, the bg engineer said it was fine to move it there.

What sort of tests can I do to see if it’s up to the job?

Thankyou

djrock
 
Sponsored Links
The physical size of the vent, although not immaterial, does not really matter. It is the amount of free air that the vent passes that counts.

For your boiler I would always install a 100cm2 vent to outside and lined through the cavity.
 
Hi, I was planning on running PVC 100mm Ducting from the outside vent to the inside vent but the trouble is there’s hardly any space to run it up to the vent due to the pipes.

Could I get away with running the ducting to the bottom of the box section? Its not too far away from the vent.

Thankyou