Hello there, can anyone help?
My boiler works fine when CH or HW, or both are selected, but as soon as they are both switched off via the timer, the boiler hunts, fan switching on and off again every couple of seconds continually, and therefore the boiler does not fire up.
I have replaced the fan and pcb. the first two leds are on and the troubleshooting chart suggests the air pressure switch should be replaced (power gets to the switch, but the 'C' connection pulses. I have checked the air tubes for blockages (both are ok) and I know the fan is ok. If I disconnect one tube from the switch, the fan runs ok. So is it the air pressure switch which is at fault?
Regards, David
My boiler works fine when CH or HW, or both are selected, but as soon as they are both switched off via the timer, the boiler hunts, fan switching on and off again every couple of seconds continually, and therefore the boiler does not fire up.
I have replaced the fan and pcb. the first two leds are on and the troubleshooting chart suggests the air pressure switch should be replaced (power gets to the switch, but the 'C' connection pulses. I have checked the air tubes for blockages (both are ok) and I know the fan is ok. If I disconnect one tube from the switch, the fan runs ok. So is it the air pressure switch which is at fault?